IGCSE · 4 · extended response

A thermistor alarm with a reversed response

Electricity and magnetism · Original GioPhysics question with a detailed, mark-by-mark answer guide.

Demand
discriminating
Marks
6
Topics
1
Answer
Complete
Explore the question data

Thermistor calibration

Supplied question data. Read the labelled axes and use the observations to test the physical model.

Vertical axis (y): Resistance / kΩ

Thermistor calibrationSupplied question data. Read the labelled axes and use the observations to test the physical model. Horizontal axis: Temperature / °C. Vertical axis: Resistance / kΩ. Exact values are available in the data table below.02468012.52537.550xy

Horizontal axis (x): Temperature / °C

Reading 1Temperature / °C: 10Resistance / kΩ: 8
Read the exact data as a table
Thermistor calibration — supplied values
Temperature / °CResistance / kΩ
108
204
302
401
500.5

These are the supplied values, not a worked answer. No fitted trend is drawn.

extended response6 marks

Optional enrichment: this challenge may extend beyond the usual syllabus depth and assumes confidence with algebra and graph interpretation. A 6.0 V supply is connected to a 2.0 kΩ fixed resistor in series with an NTC thermistor. Output voltage is measured across the thermistor by a high-resistance input. Its resistance–temperature data are supplied. The alarm activates when output falls below 2.0 V. Supplied data (Temperature / °C; Resistance / kΩ): (10, 8), (20, 4), (30, 2), (40, 1), (50, 0.5).

  1. (a)

    Find output voltage at 20°C and 40°C, and identify the temperature at which the threshold is reached.

    3 marks
  2. (b)

    Predict how the response changes if output is taken across the fixed resistor, and explain why the thermistor is not an ohmic resistor with one universal resistance.

    3 marks
Ready to self-mark?Reveal the detailed answer guide
Answer overview(a) Vout = 4.0 V at 20°C and 2.0 V at 40°C; it activates above 40°C in this ideal calibration. (b) The fixed-resistor output rises with temperature; it is 2.0 V at 20°C and 4.0 V at 40°C.
01

(a)

3 marks

Find output voltage at 20°C and 40°C, and identify the temperature at which the threshold is reached.

How to approach it

Build a chain of claim, evidence and physics reasoning. Address more than one relevant factor, identify a limitation or assumption, and finish with a conclusion that is conditional on the evidence rather than absolute.

  1. 1

    For a series divider, Vout = 6.0 Rtherm/(2.0 kΩ+Rtherm). At 20°C, this is 6(4)/(2+4) = 4.0 V.

  2. 2

    At 40°C, Vout = 6(1)/(2+1) = 2.0 V. The NTC resistance decreases as temperature rises, so the thermistor voltage also decreases.

  3. 3

    The strict 'below 2.0 V' trigger occurs above 40°C, assuming monotonic response and negligible self-heating. A real alarm needs tolerance and hysteresis specifications.

02

(b)

3 marks

Predict how the response changes if output is taken across the fixed resistor, and explain why the thermistor is not an ohmic resistor with one universal resistance.

How to approach it

Build a chain of claim, evidence and physics reasoning. Address more than one relevant factor, identify a limitation or assumption, and finish with a conclusion that is conditional on the evidence rather than absolute.

  1. 1

    The two divider voltages sum to 6.0 V, so the fixed-resistor voltage is 6.0−Vtherm.

  2. 2

    As the thermistor resistance falls, total resistance falls and current rises; the fixed-resistor voltage IRfixed therefore rises.

  3. 3

    Resistance depends strongly on temperature. Even at one bath temperature a large measuring current can cause self-heating, so a calibration requires controlled conditions and suitably low power.

Complete marking guidance

Use these worked steps alongside the part-by-part answers. They explain the method and mark allocation; they do not add extra marks.

  1. For a series divider, Vout = 6.0 Rtherm/(2.0 kΩ+Rtherm). At 20°C, this is 6(4)/(2+4) = 4.0 V.
  2. At 40°C, Vout = 6(1)/(2+1) = 2.0 V. The NTC resistance decreases as temperature rises, so the thermistor voltage also decreases.
  3. The strict 'below 2.0 V' trigger occurs above 40°C, assuming monotonic response and negligible self-heating. A real alarm needs tolerance and hysteresis specifications.
  4. The two divider voltages sum to 6.0 V, so the fixed-resistor voltage is 6.0−Vtherm.
  5. As the thermistor resistance falls, total resistance falls and current rises; the fixed-resistor voltage IRfixed therefore rises.
  6. Resistance depends strongly on temperature. Even at one bath temperature a large measuring current can cause self-heating, so a calibration requires controlled conditions and suitably low power.