Reducing grid losses while respecting transformer limits

Electricity and magnetism · Original GioPhysics question with a detailed, mark-by-mark answer guide.

Demand
discriminating
Marks
6
Topics
1
Answer
Complete
Explore the question data

Ideal transformer voltage ratio

Supplied question data. Read the labelled axes and use the observations to test the physical model.

Vertical axis (y): Secondary voltage / V

Ideal transformer voltage ratioSupplied question data. Read the labelled axes and use the observations to test the physical model. Horizontal axis: Secondary/primary turns ratio. Vertical axis: Secondary voltage / V. Exact values are available in the data table below.02500500075001.00e4010203040xy

Horizontal axis (x): Secondary/primary turns ratio

Reading 1Secondary/primary turns ratio: 1Secondary voltage / V: 250
Read the exact data as a table
Ideal transformer voltage ratio — supplied values
Secondary/primary turns ratioSecondary voltage / V
1250
102500
205000
4010000

These are the supplied values, not a worked answer. Lines join the supplied values; they are not a fitted model.

extended response6 marks

Optional enrichment: this challenge may extend beyond the usual syllabus depth and assumes confidence with algebra and graph interpretation. An ideal transformer raises an AC supply from 250 V to 10.0 kV. It delivers 20.0 kW to a transmission line with total loop resistance 5.0 Ω. Compare this with delivering the same 20.0 kW into the line at 250 V. Treat 20.0 kW as power at the sending end and use rms values. The graph supplies transformer voltage against turns ratio. Supplied model: For an ideal transformer use Vs/Vp = Ns/Np and VpIp = VsIs; wire heating is I²R. Supplied data (Secondary/primary turns ratio; Secondary voltage / V): (1, 250), (10, 2500), (20, 5000), (40, 10000).

  1. (a)

    Find turns ratio, secondary and primary currents, line loss and receiving-end power for the 10 kV case.

    3 marks
  2. (b)

    Evaluate the direct 250 V comparison and explain why a transformer does not work continuously with steady DC.

    3 marks
Ready to self-mark?Reveal the detailed answer guide
Answer overview(a) Turns ratio = 40; secondary current = 2.0 A; primary current = 80 A; line loss = 20 W; received power = 19.98 kW. (b) The naive 250 V case demands 32 kW of line loss for only 20 kW sent, revealing that the assumed delivered operating point is impossible with a passive load.
01

(a)

3 marks

Find turns ratio, secondary and primary currents, line loss and receiving-end power for the 10 kV case.

How to approach it

Build a chain of claim, evidence and physics reasoning. Address more than one relevant factor, identify a limitation or assumption, and finish with a conclusion that is conditional on the evidence rather than absolute.

  1. 1

    Vs/Vp = Ns/Np = 10000/250 = 40. At the sending end Is = P/Vs = 20000/10000 = 2.0 A.

  2. 2

    For an ideal transformer input power equals output power, so Ip = 20000/250 = 80 A.

  3. 3

    Line heating is I²R = 2²(5) = 20 W, leaving 20000−20 = 19980 W at the receiving end; the line voltage drop is IR = 10 V.

02

(b)

3 marks

Evaluate the direct 250 V comparison and explain why a transformer does not work continuously with steady DC.

How to approach it

Build a chain of claim, evidence and physics reasoning. Address more than one relevant factor, identify a limitation or assumption, and finish with a conclusion that is conditional on the evidence rather than absolute.

  1. 1

    Using sending current P/V = 20000/250 = 80 A would give a 400 V line drop and I²R = 32000 W, exceeding the sending power.

  2. 2

    This contradicts a passive receiving load at the assumed operating point; the calculation demonstrates why voltage drop and the load must be solved together, and why high-voltage transmission is useful.

  3. 3

    A steady DC current produces steady flux after the switching transient, so it induces no sustained secondary emf. Real AC transformers also have core and winding losses and insulation limits.

Complete marking guidance

Use these worked steps alongside the part-by-part answers. They explain the method and mark allocation; they do not add extra marks.

  1. Vs/Vp = Ns/Np = 10000/250 = 40. At the sending end Is = P/Vs = 20000/10000 = 2.0 A.
  2. For an ideal transformer input power equals output power, so Ip = 20000/250 = 80 A.
  3. Line heating is I²R = 2²(5) = 20 W, leaving 20000−20 = 19980 W at the receiving end; the line voltage drop is IR = 10 V.
  4. Using sending current P/V = 20000/250 = 80 A would give a 400 V line drop and I²R = 32000 W, exceeding the sending power.
  5. This contradicts a passive receiving load at the assumed operating point; the calculation demonstrates why voltage drop and the load must be solved together, and why high-voltage transmission is useful.
  6. A steady DC current produces steady flux after the switching transient, so it induces no sustained secondary emf. Real AC transformers also have core and winding losses and insulation limits.